We have 5 Distribution sections with variable loads&We have 3 Gensets(500kva,380kva&250kva) our total load is between 400kva to 600kva. so how could we connect 3gensets.

5 Antworten

Relevanz
  • vor 1 Jahrzehnt
    Beste Antwort

    Probably easiest to rectify it, then invert it back to AC. Especially if the generator sets were never designed to be synchronised in the first place.

    Alternatively, you could re-arrange your loads. That way you could even probably get rid of one of the generator sets altogether.

  • vor 1 Jahrzehnt

    Use the 2 smaller gensets so they keep a high load on each. Once they are synched together, adjusting the speed of one and not the other will pull more load onto that generator.

    Quelle(n): Engineering College
  • Anonym
    vor 1 Jahrzehnt

    Generators can be connected in parallel when properly synchronized. Each unit should have the same terminal voltage, the same frequency, same phase sequnce. The generators should be synchronized to a common switchboard with an automatic synchronizer.One unit used as the common standard connected first to the switchboard and the other units are synchronized one after another to the common switchboard.

    Quelle(n): Industrial plant experience.
  • Numbat
    Lv 6
    vor 1 Jahrzehnt

    You will need automatic equipment to synchronize and maintain phase lock on all generators. Such equipment is called a Synchroscope.

    It is not possible to connect two AC power systems unless the systems are synchronized.

  • Wie finden Sie die Antworten? Melden Sie sich an, um über die Antwort abzustimmen.
  • Anonym
    vor 1 Jahrzehnt

    You have to go for an auto-synchronisation and auto-load sharing system.